Static phase converters suck.
In my situation with low HP machines, Bridgeport and Harig surface grinder, I had good results with static converters. They were an inexpensive solution , easy to wire and served me well.

Now if I was running large industrial machines running lots of hours and hogging big chips the rotary converters would have been the way to go.
 

TheOldHokie

Well-known member
Lifetime Member

Equipment
L3901/LA525, G2160/RCK60, G2460/RCK60
Apr 6, 2021
10,847
5,957
113
Myersville, MD
windyridgefarm.us
Sorry, that is an internet myth, 100% not true for VFD's.

I have three of them...not an 'expert' by any means, but plenty of experience with them.
No internet myth. Here are some experts explaining why. Pay close attention to Forrest Addy who is an expert of experts.


You will find that same info straight from the OEM sites


Basically when using single phase input you are increasing input current draw on L1 and L2 beyond the 3 phase design rating. You have to be very careful when shopping to read the manufacturers fine print. Most headline ratings are for 3P input and the derating number is hidden in the fine print.

Dan
 

TheOldHokie

Well-known member
Lifetime Member

Equipment
L3901/LA525, G2160/RCK60, G2460/RCK60
Apr 6, 2021
10,847
5,957
113
Myersville, MD
windyridgefarm.us
In my situation with low HP machines, Bridgeport and Harig surface grinder, I had good results with static converters. They were an inexpensive solution , easy to wire and served me well.

Now if I was running large industrial machines running lots of hours and hogging big chips the rotary converters would have been the way to go.
It depends on the converter.

I say they suck because with most low cost units you only get 2/3 the rated motor HP and the motors run hot when loaded. The cheap units are simply motor starters and you are actually running the motor on just two of the three legs. Not at all good for the motor. Better ones also have run caps and you get a third leg and about 80% power. At this point you have an RPC minus the idler motor. Adding an idler motor gets you an RPC, roughly 98% power and better balanced legs.

Higher end solid state converters generate quality three leg power and are a different and much more costly animal.
 
Last edited:
  • Like
Reactions: 1 user

John T

Well-known member

Equipment
2017 BX23S
May 5, 2017
1,096
582
113
under a rock
You would be shocked at the cost of that service.
I'm sure your right.

So, what is the advantage of a 3ph machine?
Other than they are cheaper because very few folks can power them.... (correctly)

I mean, for a hobbiest guy wouldn't it be more practical to buy a single phase machine OR swap out the motor for a single phase lump?
That has to be possible... No?
 

TheOldHokie

Well-known member
Lifetime Member

Equipment
L3901/LA525, G2160/RCK60, G2460/RCK60
Apr 6, 2021
10,847
5,957
113
Myersville, MD
windyridgefarm.us
I'm sure your right.

So, what is the advantage of a 3ph machine?
Other than they are cheaper because very few folks can power them.... (correctly)

I mean, for a hobbiest guy wouldn't it be more practical to buy a single phase machine OR swap out the motor for a single phase lump?
That has to be possible... No?
There are a multitude of advantages to 3 phase induction motors. Ask Google for a list.

But the biggy is single phase motors top out around 5-7 HP and even at that relatively small size require "massive' input current draws.

Take a look at the big green mill in my earlier post. It has 4 motors, a 7.5HP main spindle, a 3 HP vertical head, a 3HP knee motor, and a 1/8 HP coolant pump. Converting it and all the electrical controls to single phase is not practical but powering it with a El Cheapo DIY rotary phase converter is.

Dan
 
Last edited:
  • Like
Reactions: 1 user

Russell King

Well-known member
Lifetime Member

Equipment
L185F, Modern Ag Competitor 4’ shredder, Rhino tiller, rear dirt scoop
Jun 17, 2012
7,020
2,475
113
Austin, Texas
I had the same problem with my lathe. The motor was wired for 400V three phase star configuration and I changed that to delta, making it 230V three phase. I use Toshiba inverters for the conversion from single phase 230V to 230V three phase. I am not using variable frequency but only the soft start (programmable) that I also use on the hydraulic pump of the pillar lift. I simply have the on/off function and the speed change is using the various gears.
Just to clarify…How many converters did you use? If more than one why?

I can swear when I was discussing the use of small single phase input converters to get three phases out I was told by a power electronics engineer that more than one would be required but I may have been understanding this incorrectly or maybe it was to change the voltage also and go to three phases. I was just discussing it casually as in ”is that possible and what people are doing now”.

I worked at an electric motor (large industrial motors - usually 4000V 3 phase) that also designed and built adjustable speed converters to drive the motors. So they would commonly use “more slices” to increase power output where a slice was similar to a slave drive that all communicated to each other through a master control slice that was the “brains” that controlled most everything.

As a mechanical engineer they were interesting devices that just made my job a bit more complicated due to the various speeds the motors could be operated on (two pole motors on 60 Hz power usually went through the first critical shaft speed and ran fine at 3600 RPMs but not well at 70 to 80% synchronous speed for example)
 

TheOldHokie

Well-known member
Lifetime Member

Equipment
L3901/LA525, G2160/RCK60, G2460/RCK60
Apr 6, 2021
10,847
5,957
113
Myersville, MD
windyridgefarm.us
Just to clarify…How many converters did you use? If more than one why?

I can swear when I was discussing the use of small single phase input converters to get three phases out I was told by a power electronics engineer that more than one would be required but I may have been understanding this incorrectly or maybe it was to change the voltage also and go to three phases. I was just discussing it casually as in ”is that possible and what people are doing now”.

I worked at an electric motor (large industrial motors - usually 4000V 3 phase) that also designed and built adjustable speed converters to drive the motors. So they would commonly use “more slices” to increase power output where a slice was similar to a slave drive that all communicated to each other through a master control slice that was the “brains” that controlled most everything.

As a mechanical engineer they were interesting devices that just made my job a bit more complicated due to the various speeds the motors could be operated on (two pole motors on 60 Hz power usually went through the first critical shaft speed and ran fine at 3600 RPMs but not well at 70 to 80% synchronous speed for example)
In the class of motors abd inverters we are talking about an inverter produces 3 phase output. Period. You only need one to convert 240v single phase input to 240v 3 phase output.

If your machine has mulltiple motors and you want to use the inverter to CONTROL each one separately you need multiple inverters - one for each motor.

Dan
 
Last edited:

Sidekick

Well-known member

Equipment
Kioti CK2620SE cab, RTV-X, BX2360, Z726XKW-3-60
Jul 29, 2023
1,098
1,547
113
N.Y,
I have been running my Bridgeport on a static phase controller for 30 years without a problem but getting ready to switch to a VFD. For my CNC spindles I use Chinese VFDs. I switched to a single phase motor on my southbend lathe.
 

InTheWoods

Active member

Equipment
B7510/FEL, B7100D, ZD18, ASK-R130
Nov 17, 2023
266
215
43
Indiana
When I first got my vertical mill, I built a rotary phase converter for it. It was fine and, at the time, the least expensive way to go. I long ago ditched the RPC and switched to VFD (actually two VFDs - one for the feed motor and one for the spindle). Hell - I've put VFDs on my belt sander and bandsaw too...

Hooking up a VFD takes a different skill set than building a rotary phase converter - a skill set that involves reading and understanding the Chinglesh owner's manual that'll come with the VFD. But lots of folks have done it.

Anyway - get the VFD. All the cool kids are doing it...
 
  • Love
Reactions: 1 user

Lil Foot

Well-known member
Lifetime Member

Equipment
1979 B7100DT Gear, Nissan Hanix N150-2 Excavator
May 19, 2011
7,968
3,269
113
Peoria, AZ
My mill is 2hp 220v 3 phase, powered with a Phase-a-matic PAM-300 solid state 1 phase to 3 phase converter.
It has run flawlessly for over 30 years.
I pulled the power from an unused 30a 220v dryer circuit.
I'm told that this setup will provide less than full power, but I have never been able to detect any evidence of that.
I also run my 220v 3 phase diamond/alox tool grinder on the same circuit, but not at the same time.
I have a 12-4 rubber cord from the converter connected to the mill through a 20A 250V 3 phase twist lock cord cap, and just disconnect it from the mill and connect it to the grinder's cord with the same cord/cap.
I forward/reverse power tap with large taps (1"-8 UNC & 1"-12 UNF) and have taken heavy enough cuts to make the belt slip with no problems from the converter.

I suppose if I had it to do over again, I might go with a VFD, but this was cheap & fast to acquire & hook up.
I think I installed it & was up and running in less than an hour after the converter was delivered.
 
  • Like
Reactions: 1 user

Lil Foot

Well-known member
Lifetime Member

Equipment
1979 B7100DT Gear, Nissan Hanix N150-2 Excavator
May 19, 2011
7,968
3,269
113
Peoria, AZ
When the company closed down the quartz research lab I worked in, I considered buying the 11-20 Blanchard grinder for personal use.
I contacted the local power company about bringing in power for it, and when they got through laughing, they told me it would be cheaper for me to buy a property in an industrial area that already had the power the grinder needed.
If I remember right, it was 480V, 60A, 3 phase.
20hp spindle, 14hp table drive, 8hp spindle feed, 4hp coolant pump.

Sigh, it was a fabulous machine.
Blanchard_11-20_Kyo__1a_.JPG
 
  • Like
Reactions: 1 user

Runs With Scissors

Well-known member

Equipment
L2501 TLB , Grappel, Brush Hog, Box Blade, Ballast box, Forks, Tiller, PH digger
Jan 25, 2023
3,367
4,296
113
Michigan
WOW guys, thanks for all the info.

Looks like I have some “homework” to do.

So this whole “power tapping” thing looks to me like it would "hurt the machine”.

From a beginners perpsctive, doesn’t that "instant reversing" damage the gears of the machine?

I have seen lots of videos of people doing it, but I still have a hard time wrapping my head around how in the world that can be OK to do to a machine. And would I miss not having the capability???????





BTW - your understanding of C is waaaay off the mark.
Yes sir, you are probably right about that. Hence my question.

I’m a “Cherry Boy” when it comea to 3 phase power. (y)

I’m still reading through the plethora of material provided by y’all, and have not ruled out anything yet.

@TheOldHokie do you have any recommendations for building one of these? (i.e. brands to get or stay away from? Are they loud? )






Two options


I bought a digital phase converter 20 years ago.
Set it up in my shop wired the output to a 3 phase panel.
Wired my whole 3 phase shop to the panel .
I have moved twice since then and it all came with me.
I have had zero problem with this setup.
It comes with a price though. 20HP converter in 2005 was $6000.00
I was running 2 CNC machining centers, compressor, grinder, lathe etc.

If this is going to be your only need for 3 phase....
eliminate the need.


The bottom option is very intriguing. I currently have a 1 HP machine, so “technically” I would be upgrading my HP…..(although it’s a Chi-Com motor so…..:unsure:)


Attention VFD proponents……..

Since I have no experience with VFD’s, any reccomendations on brands? I obvouisly went to Amazon and started looking.

Lots of “cheap options” but they almost seem “too good , to be true” ……


Thanks for the help/advice/opinions so far though…….🍻
 

Runs With Scissors

Well-known member

Equipment
L2501 TLB , Grappel, Brush Hog, Box Blade, Ballast box, Forks, Tiller, PH digger
Jan 25, 2023
3,367
4,296
113
Michigan
My mill is 2hp 220v 3 phase, powered with a Phase-a-matic PAM-300 solid state 1 phase to 3 phase converter.
It has run flawlessly for over 30 years.
I pulled the power from an unused 30a 220v dryer circuit.
I'm told that this setup will provide less than full power, but I have never been able to detect any evidence of that.
I also run my 220v 3 phase diamond/alox tool grinder on the same circuit, but not at the same time.
I have a 12-4 rubber cord from the converter connected to the mill through a 20A 250V 3 phase twist lock cord cap, and just disconnect it from the mill and connect it to the grinder's cord with the same cord/cap.
I forward/reverse power tap with large taps (1"-8 UNC & 1"-12 UNF) and have taken heavy enough cuts to make the belt slip with no problems from the converter.

I suppose if I had it to do over again, I might go with a VFD, but this was cheap & fast to acquire & hook up.
I think I installed it & was up and running in less than an hour after the converter was delivered.
So you are using "Method 1” in their description?

METHOD #1

Using the Phase-A-Matic™ Static Converter only will produce approximately 2/3 normal HP.* This method is inexpensive, the most popular, provides excellent results on most machines tools and numerous other uses. Motor speed is not changed. Most two-speed motors, power feeds, coolant pumps, etc., will operate normally. Motor will instant reverse. There is nothing to change. All switch gear will work normally. *Refers to wye-wound motors; delta-wound motors will run at 50% rated HP. Delta-wound motors are very rare in the USA, occasionally being found on some imported equipment, and are particularly found on German and Italian machines.
 

Runs With Scissors

Well-known member

Equipment
L2501 TLB , Grappel, Brush Hog, Box Blade, Ballast box, Forks, Tiller, PH digger
Jan 25, 2023
3,367
4,296
113
Michigan
Sorry for the silly question but, Do you have 3 phase on your street?
If so It might be worth it to have the power company run it to the house...
We do not.

I live in a typical residential subdivision.
 

TheOldHokie

Well-known member
Lifetime Member

Equipment
L3901/LA525, G2160/RCK60, G2460/RCK60
Apr 6, 2021
10,847
5,957
113
Myersville, MD
windyridgefarm.us
WOW guys, thanks for all the info.

Looks like I have some “homework” to do.

So this whole “power tapping” thing looks to me like it would "hurt the machine”.

From a beginners perpsctive, doesn’t that "instant reversing" damage the gears of the machine?

I have seen lots of videos of people doing it, but I still have a hard time wrapping my head around how in the world that can be OK to do to a machine. And would I miss not having the capability???????







Yes sir, you are probably right about that. Hence my question.

I’m a “Cherry Boy” when it comea to 3 phase power. (y)

I’m still reading through the plethora of material provided by y’all, and have not ruled out anything yet.

@TheOldHokie do you have any recommendations for building one of these? (i.e. brands to get or stay away from? Are they loud? )









The bottom option is very intriguing. I currently have a 1 HP machine, so “technically” I would be upgrading my HP…..(although it’s a Chi-Com motor so…..:unsure:)


Attention VFD proponents……..

Since I have no experience with VFD’s, any reccomendations on brands? I obvouisly went to Amazon and started looking.

Lots of “cheap options” but they almost seem “too good , to be true” ……


Thanks for the help/advice/opinions so far though…….🍻
You can.build a 2 HP rotary phase converter yourself using a used 2HP 3 phase idler motor and a handfull of capacitors. Its cheap, provides clean 3p power and full load motor HP. Just plug the Bridgeport in and it will operate exactly as it was designed. Did you get one with a variable speed head? If not thats the only advantage to using a VFD.

Three phase motors are self reversing. My Cincinnati has a push button on the end of the quill feed lever for reversing the spindle when doing rigid tapping operations. There are also adjustable travel stops on the quill that allow you to set the depth for repeated operations and the machine automagically does it for you. Its a bit noisy but at tapping spindle speeds there is no risk of damage to the machine.

I will be happy to walk you through a build. Its not complicated and you will come away with a nuch clearer understsndung of how 3P power works. At least investigate what you do and dont get with the various options. If using a static converter be very carrful about what you buy. The cheap ones are just a start cap in a box snd you are actually running the notor with single phase power. Thats a FAULT condition that a VFD would sense and shutdown the motor.
 