Non tractor - Electrical question

fried1765

Well-known member

Equipment
Kubota L48 TLB, Ford 1920 FEL, Ford 8N, SCAG Liberty Z, Gravely Pro.
Nov 14, 2019
7,843
5,066
113
Eastham, Ma
I have a new Duromax 8500W generator on the way.
It has a FOUR prong 30A/240V output twist lok..
I want to run a 15'- 8ga. cord to what is now a 30A/240V- 3 prong wall receptacle.
Internet says that current 3 prong must be changed to 4 prong receptacle.
I am Ok with doing that, but do not understand the benefit.

The existing (600' long underground) wiring is 2 hots and a neutral, but NO GROUND.
What should I connect that 4th prong to, when I replace the 3 prong wall receptacle, with 4 prong?
 

DaveFromMi

Well-known member

Equipment
L3901 RCR1260
Apr 14, 2021
610
530
93
Indiana
If you ground the generator frame, you can get by with 3 wires. There are 2 hot wires, a neutral and a ground for the 4 wire receptacle.
 

WFM

Well-known member
Premium Member

Equipment
L3800
Apr 5, 2013
1,342
671
113
Porter Maine
Not to answer your question. But my cord was already 4 wire. So one end is 30 amp twist for the new generator the other end is a 50 amp wall plug. For mine. But not sure your three wire will work where you need 4.
I did add four 5" all swivel locking casters to my giant Duromax one.
 

Attachments

fried1765

Well-known member

Equipment
Kubota L48 TLB, Ford 1920 FEL, Ford 8N, SCAG Liberty Z, Gravely Pro.
Nov 14, 2019
7,843
5,066
113
Eastham, Ma
If you ground the generator frame, you can get by with 3 wires. There are 2 hot wires, a neutral and a ground for the 4 wire receptacle.
OK, I can certainly drive a ground rod for the generator frame.
The question remains,......what to do with that 4th pin on the generator output.
Leave it empty, ........and use ONLY the2 hots and neutral, over to the existing 3 prong wall receptacle, and use the 3 prong wall receptacle?
THAT kinda does make sense to me!
 
Last edited:

DustyRusty

Well-known member

Equipment
2020 BX23S, BX2822 Snowblower, Curtis Deluxe Cab,
Nov 8, 2015
6,237
4,816
113
North East CT
You can change the wall outlet to a 4 prong receptacle. 2 120 volt wires, 1 neutral wire, and one ground wire. Drive a copper clad ground wire into the ground and attach a #10 wire from the receptacle to the ground rod.
I have a 200 amp service disconnect behind the meter socket and then it goes into my main panel in the cellar. By code I had to separate the grounds and neutrals, and run a copper ground wire from the panel out to the well casing. When the service was originally installed there was a requirement for a ground rod in the cellar that bonded to the neutral and the ground wires in the panel. When I was required to separate the grounds and neutrals, I was told that I should "hit" every ground rod that was previously used and keep going until I finally made it to the steel well casing and it should be bonded to the casing. The way that it was originally laid out, I had 3 ground rods, and when the meter was moved, I installed a 4th under the meter socket. That copper wire is one continuous wire through the clamps on all 4 ground rods, and it is bonded to the well casing. The Utility (CL&P) installed a ground rod at the base of the pole where the transformer is located bringing the total number of ground rods to 5.
The ground rods are to capture any failure of the neutral wires in the system.

Edit: I misread the original post, but after reading it a second time, I believe that you are going to be back feeding the electrical pane with the generator through a 3 prong receptacle. Is this correct? Are you installing a service disconnect on the service panel or are you going to be turning off the main circuit breaker when using the generator?
 
Last edited:

fried1765

Well-known member

Equipment
Kubota L48 TLB, Ford 1920 FEL, Ford 8N, SCAG Liberty Z, Gravely Pro.
Nov 14, 2019
7,843
5,066
113
Eastham, Ma
You can change the wall outlet to a 4 prong receptacle. 2 120 volt wires, 1 neutral wire, and one ground wire. Drive a copper clad ground wire into the ground and attach a #10 wire from the receptacle to the ground rod.
I have a 200 amp service disconnect behind the meter socket and then it goes into my main panel in the cellar. By code I had to separate the grounds and neutrals, and run a copper ground wire from the panel out to the well casing. When the service was originally installed there was a requirement for a ground rod in the cellar that bonded to the neutral and the ground wires in the panel. When I was required to separate the grounds and neutrals, I was told that I should "hit" every ground rod that was previously used and keep going until I finally made it to the steel well casing and it should be bonded to the casing. The way that it was originally laid out, I had 3 ground rods, and when the meter was moved, I installed a 4th under the meter socket. That copper wire is one continuous wire through the clamps on all 4 ground rods, and it is bonded to the well casing. The Utility (CL&P) installed a ground rod at the base of the pole where the transformer is located bringing the total number of ground rods to 5.
The ground rods are to capture any failure of the neutral wires in the system.

Edit: I misread the original post, but after reading it a second time, I believe that you are going to be back feeding the electrical pane with the generator through a 3 prong receptacle. Is this correct? Are you installing a service disconnect on the service panel or are you going to be turning off the main circuit breaker when using the generator?
You have answered my question!
Thank you!
My arrangement likely will be described in somewhat nasty terms by others here on OTT.
I will be tripping the main and back feeding.

I have done this MANY times prior.
I use a checklist!
No other person will have access to the generator.
I have lived my life with checklists!
I have 30,000+ hours of flight time.......ALL with the use of checklists!
Some of my early flight experience included using checklists to land safely aboard an aircraft carrier.
At 83+, I am still alive,.......thanks to my using, and understanding, the importance of checklists!

I am presently thinking that I shall replace the 3 prong receptacle with a 4 prong, and run a #10 bare ground from that ground terminal to a copper clad ground rod.
 
  • Like
Reactions: 1 user

Daferris

Well-known member

Equipment
LX2610
Nov 23, 2021
483
403
63
Mid-Michigan
I suggest watching some of the videos that Mike Holt has about grounding and bonding. this is a link to one of his youtube's