dvcochran
Active member
Equipment
Kubota M9000, New Holland TN90, Deere 2640, Vermeer 504N, Vermeer 504SI, more
On the ones you changed out, had they totally failed (not working at all) or were they not working within the temperature/pressure specs?in addition, its possible that the thermostatic switch could have been the problem all along....I don't know this but I'll explain.
When (if) the evap freezes over, airflow drops, and refrigerant is in liquid state. With no warm air flowing over the evap, there is a chance the liquid refrigerant could get back to the compressor which will destroy the compressor.
yes I have had to replace one or two of those thermostatic switches. Been several years since I seen the last one.
I have been pulled away from this project and hope to get back on it this week. I have looked over the WSM and will check the chare and cycling of the two switches.
To be clear, IF the charge is correct and there are no other problems, the dual type pressure switch (10-54 in WSM) should always be in the ON (B) position? Or should it eventually go to position (C) as pressure builds in a 'normal' cycle?
The thermostatic switch, which is in series with the pressure switch, is purely a failsafe to prevent the evaporator from freezing over? With my discharge temp so high, unless it is opening very early I more suspect the pressure switch at this point.
I have to put the gauges on and pull the roof.
Any other suggestion?