This is interesting and I will need some time to digest and think about it...thanks for posting!Earth "grounds" are different ......even though that sounds CRAZY as hell. In a house, there is typically a "ground" and the meter base or a ground via an underground "pipe" or both.
A ground at the house is not the same as a ground 125' away - I know that sounds weird..... the point really is this - electricity is a lot like water, spill water- it will FIND the lowest point on the floor/ground ....
Electricity will FLOW to the "easiest" way back to ground.......
for that reason you want to have a separate ground at a "new" sub panel.
Here is more on the subject manner:
copy and pasted
Rule #1: The grounded conductors (neutrals) and the equipment grounds must always be isolated after the main service panel. There are two essential reasons for this rule:
To provide a low-resistance path for current travel to the transformer in the event of a ground fault. This path should not be energized to ensure that it is fully available for the fault current in the event of a malfunction.
To prevent the ground wires from conducting returning neutral current during normal operation. Neutral current in the equipment ground wires can energize the casings and enclosures of appliances and equipment.
Rule #2: In a subpanel, the terminal bar for the grounded conductors (commonly known as the neutral bus) should always be insulated from the enclosure. The reason for this rule is to prevent the enclosure from conducting current.
Edit: First thought is why should a sub panel in a house be different than a sub panel in a shed not far away?
Keep thinking they should be the same, as a sub panel is a sub panel...
Need to keep thinking at my end...Thanks again...