I should remember why, but I don't. So I will ask.
IF one were to run 4,4,4,4 wire to the sub panel (or whatever size was needed, but all the same), why should ground rods at the sub panel be needed/required? 4 individual conductors, not a built up wire that is not likely available in that configuration.
The safety ground would carry any ground current back to the ground rods connected to the incoming service entrance panel. And would have the same capacity as the power carrying conductors.
I am pretty sure I was not required to use a ground rod(s) when installing a sub panel in my home, in the basement at the opposite side of the house. So if this is correct, why would a sub panel in the shed not far from the home require ground rods, if all four conductors connected to it are the same size?
I can see a possible reason if the forth wire is smaller in size...But in the case of my question, all four conductors are the same gauge.
Earth "grounds" are different ......even though that sounds CRAZY as hell. In a house, there is typically a "ground" and the meter base or a ground via an underground "pipe" or both.
A ground at the house is not the same as a ground 125' away - I know that sounds weird..... the point really is this - electricity is a lot like water, spill water- it will FIND the lowest point on the floor/ground ....
Electricity will FLOW to the "easiest" way back to ground.......
for that reason you want to have a separate ground at a "new" sub panel.
Here is more on the subject manner:
copy and pasted
Rule #1: The grounded conductors (neutrals) and the equipment grounds must always be isolated after the main service panel. There are two essential reasons for this rule:
To provide a low-resistance path for current travel to the transformer in the event of a ground fault. This path should not be energized to ensure that it is fully available for the fault current in the event of a malfunction.
To prevent the ground wires from conducting returning neutral current during normal operation. Neutral current in the equipment ground wires can energize the casings and enclosures of appliances and equipment.
Rule #2: In a subpanel, the terminal bar for the grounded conductors (commonly known as the neutral bus) should always be insulated from the enclosure. The reason for this rule is to prevent the enclosure from conducting current.