We just recently moved closer to the coast and now must prepare for hurricanes. Since, there are so many helpful and knowledgable folks on this forum i thought I would throw out this question.

I bought a Champion generator rated for 10k watts up to 11,500 starting watts.. The house we bought has a transfer switch where I can run the power through my main panel. my question is where can I buy a cord that will connect my generator to the transfer switch? The ones I found on line and at big box stores are rated up to 7500 watts
 

NCL4701

Well-known member

Equipment
L4701, T2290, WC68, grapple, BB1572, Farmi W50R, Howes 500, 16kW IMD gen, WG24
Apr 27, 2020
2,798
4,246
113
Central Piedmont, NC
For something that size or bigger it’s probably either buy the appropriate plugs and correct wire size for your length of run and make up a cord yourself or get a local electrician to make up a cord. I had the electrician make the cord for my 16kW generator when he installed the transfer switch. He was able to source materials for less than I could so cost to have him do it was about the same as it would have been for me to do it myself.
 
  • Like
Reactions: 1 users

Tughill Tom

Well-known member

Equipment
B3200
Dec 23, 2013
1,217
1,344
113
Turin, NY
We just recently moved closer to the coast and now must prepare for hurricanes. Since, there are so many helpful and knowledgable folks on this forum i thought I would throw out this question.

I bought a Champion generator rated for 10k watts up to 11,500 starting watts.. The house we bought has a transfer switch where I can run the power through my main panel. my question is where can I buy a cord that will connect my generator to the transfer switch? The ones I found on line and at big box stores are rated up to 7500 watts
You'll need to know the NEMA # of the plug on your gen set and the total amps. Same on the transfer switch, they will need to be the same size. Then find the wire size you'll need to size up the cord and then buy what you need.
 

WhitleyStu

Active member
Premium Member

Equipment
B2601 LA435 FEL 60" MMM 60" Snow Blower FSP500 Spreader 5' Grahl Roller 40 spray
Sep 10, 2020
58
103
33
Indiana
I have 10' of Coleman Cable 4-4 SEOW 600V P-241-3-MSHA coming out of the transfer switch with a NEMA 14-60P 60A plug on it to plug into the generator's receptacle. My generator is a 13,500 watt.
 

BAP

Well-known member
Lifetime Member

Equipment
2012 Kubota 2920, 60MMM, FEL, BH65 48" Bush Hog, 60"Backblade, B2782B Snowblower
Dec 31, 2012
2,756
867
113
New Hampshire
Search online, there are many sources if you want to go that route. Getting one made up may be cheaper. Here is one place.