That's what I will do! Thanks for the inputs60 amp circuit breaker with min 10 gauge is preferred but I’d run 8. I work on these everyday. Incoming rush will take a motor out if not properly sized.
That's what I will do! Thanks for the inputs60 amp circuit breaker with min 10 gauge is preferred but I’d run 8. I work on these everyday. Incoming rush will take a motor out if not properly sized.
Started a brand new 5 HP compressor today. Incoming rush 109 amps. Customer was speechless. He had a 30 amp breaker with 12 or 14 gauge wire. Before I left he was going to run a 50 amp breaker with 8 gauge wire. Should be much better for him in the long run. Just food for thought.That's what I will do! Thanks for the inputs
Maybe you should educate me a bit. Let say I do use a 8 gauge wire, to put a 30 circuit breaker will not hurt my system right, breaker will trip if there is a short or overload, like I said maybe I am wrong.Started a brand new 5 HP compressor today. Incoming rush 109 amps. Customer was speechless. He had a 30 amp breaker with 12 or 14 gauge wire. Before I left he was going to run a 50 amp breaker with 8 gauge wire. Should be much better for him in the long run. Just food for thought.
A run of 8 gauge and 30 amp breaker will work just fine. I run my 3hp tablesaw on a 30 amp breaker with 10 gauge wire without any trouble of a breaker tripping.Maybe you should educate me a bit. Let say I do use a 8 gauge wire, to put a 30 circuit breaker will not hurt my system right, breaker will trip if there is a short or overload, like I said maybe I am wrong.
So why a bigger circuit breaker?
I just need to understand
not worried, just need to understand better.Fluke631, if you are really concerned about the wiring you can get an electrical permit and have it inspected by the ESA.
Thanks Magicman!There is no problem as long as the wiring has a higher amp rating than the breaker.
Thanks a lot for clarifications, yes I do have a 30 breaker (double post of course) on hand and 8 gauge wire. Because I am not an electrician I figure I could ask here and to be honest I was a bit confused about the proper size circuit breaker after reading some posts. Thanks a lot for the great information.It always surprises me when I read/hear people who believe a circuit breaker protects the appliance or that the appliance wiil be damaged by an improperly rated CB.
It’s time for everyone to understand that a CB’s only purpose is to protect the WIRE which serves the appliance. So a CB should be rated based upon the gauge of WIRE. The CB does NOT protect the appliance.
The gauge of WIRE should be sized/rated appropriate to the expected electrical demand of the appliance. Good practices dictate that the wire should be rated 120% above the max electrical demand of the appliance.
So,... if the appliance needs 21.5 Amps then the next size wire ga UP should be selected for 120% of 21.5A which is 25.8A Here’s a chart to assist you:
https://www.cerrowire.com/products/resources/tables-calculators/ampacity-charts/
Notice that the ambient temperature should be considered.
Notice that the choice of conductor can affect matters (copper vs aluminum).
I suggest 8ga wire and a 30 Amp CB.
OP, I see you think you have “on hand” a 30A breaker. I hope you realize 230 volt circuit will require a “double” breaker.
Keep in mind that old breakers can lose their calibration. Some old breakers (and their cabinets) should be CONDEMNED (such as Federal-Pacific. See: https://www.angieslist.com/articles/are-federal-pacific-circuit-breaker-panels-safe.htm )
Hope this helps.
I would be more worried about the wire size and length of wire ran to the machine. Smaller wire causes voltage drop. I have also seen breakers that were not sized properly and overtime heated up internally causing an electrical arc or melt down. I was recommending to you what I have seen in the field that works the best with little to no issues. Everyone has their own opinion. For a typical home compressor this is what I recommend to every home owner and they have had years of dependable equipment. I watched a man run 14 gauge wire 200 feet from his house to the compressor and wondered why it didn’t run. The voltage dropped from 230 to 115 before tripping the breaker. Hope this helps.Thanks a lot for clarifications, yes I do have a 30 breaker (double post of course) on hand and 8 gauge wire. Because I am not an electrician I figure I could ask here and to be honest I was a bit confused about the proper size circuit breaker after reading some posts. Thanks a lot for the great information.
Exactly! Good point Jaythe 'hoses' numbers also apply to gardening !! Wife didn't understand that ONE 1000' length of 1/2" weeping hose wouldn't water her garden. I broke it into 8 , 150+-' runs, fed from 1 1/2" header from 2" feed from tank.