Back in the day of R12, you just loaded a can of gas in and rolled.
The oil for R134a sucks up moisture 100 times that of R12's.
It's a three-prong approach for R134a. Vacuum does not remove enough moisture. The drier must be replaced every time the system is opened and is considered disposable. And a dry inert gas is used for additional drying.
Vacuum standard is now 500 microns. However, Tecumseh recommends 200 micron for their products using R134a. Vacuum is to be pulled from both low and high side at the same time. Once pulled down to target (200, 300, 500 micron) wait at least 10 minutes while observing the pressure. Moisture will cause the gauge to go up (towards atmosphere). Because vacuum is not sufficient by itself, dry nitrogen is added to further remove moisture and to break the vacuum for another attempt.
Only after the pressure stabilizes should an attempt be made to charge refrigerant. It may take as long as it takes.
I would try to find that leak before changing the expansion valve. Once the leak is fixed, then replace the components and leak test by pressure from the nitrogen and watching the gauge. Then nitrogen can be released to atmosphere (EPA allowed, no animals hurt during this) and vacuum pump started.
Your A/C guy may need some extra hoses and fittings if he does not usually use nitrogen. Once used for R134a, they can't be used for other refrigerants (because of the oils).