M7040 - AC works but blows hot after a while

Flintknapper

Well-known member
Premium Member

Equipment
L2350DT
May 3, 2022
1,767
2,226
113
Deep East Texas
You are right, I did not think to detail the procedure I followed for recharging it. It had the hole in the evap when I purchased it, so we can probably assume it was like that long enough to where the system had reached 100% equilibrium with the outside.
Here's what I did (after installing new drier, evap and exp valve):

1. Pulled vacuum, left pump on for for almost 2h while doing this.
2. Turned pump off and closed system down to observe if it would hold negative pressure, waited 1h plus - no change.
3. Filled with nitrogen, and pulled vacuum again, times 4 (I was advised to do this by someone who works with ACs, but I admit I did not look up exactly what this would achieve, I just did it because it sounded like a good idea lol)
4. Finally recharged with the refrigerant, and I also put in a little dye and some PAG oil, which was mostly guesstimated yes. Refrigerant is R134a. 2.09 lbs (I weighed it, and tried to get as close to 2.09 lbs as possible as per tractors stated capacity).

It is definitely possible the compressor is corroded on the inside. In hindsight I wish I would have replaced it as well.

Today I ran it hot and then poured some cold water on the condenser. This had the effect of dropping the output temp from 80 to 60 in just 2-3 minutes. I don't know if this means the compressor is fine, or if it might still be the culprit (or one of the culprits).

Thanks!
IF you used a rented vacuum pump then always replace the oil in the pump for best results removing moisture from the system. Always shut off all valves (manifold gauges and valves at pump) BEFORE shutting down the pump.

If the system held vacuum (28inHg) or better then you were fine. If you purged the lines correctly...then there should not have been any significant amount of air introduced.

Sounds like you charged it correctly. If the compressor were weak or failing it would show as low pressure on both the low and high side.

IF you had a restriction, you would see higher than normal high side pressure and lower than normal low side pressure (even going into vacuum).

As previously mentioned I would turn my attention first to air flow issues. Make sure the fan belt (if belt driven) is tight and not slipping. Make sure all components (Radiator, Condenser, oil coolers) are clean and do not have the fins bent or dirty.

And most importantly.....check the fan shroud to see that air is not escaping around it and the radiator.
 

DustyRusty

Well-known member

Equipment
2020 BX23S, BX2822 Snowblower, Curtis Deluxe Cab,
Nov 8, 2015
6,237
4,816
113
North East CT
When cleaning an evaporator or condenser you can't just blow it clean, you have to properly clean it with a detergent. I use Simple Green foaming coil and condenser cleaner. It is available at Home Depot.
 
  • Like
Reactions: 1 user

btcfarmer

New member

Equipment
Kubota M7040, Kubota SVL 95-2S, Volvo EC290B
Apr 9, 2024
25
9
3
Central Florida
I was going to make a suggestion, however, all the things that I thought of have already been mentioned. When I do AC work I pull a vacuum for a minimum of 24 hours, and then charge with nitrogen and note the pressures. If it holds the nitrogen for another 24 hours I will charge the system weighing the refrigerant as I install it. Most times I will put 80% of the stated refrigerant into the system, and then run the system watch the gauges, and slowly add refrigerant on the low side until I get the gauge readings that are shown in the service manuals. The only thing I can think of that hasn't been mentioned is whether you wrapped the expansion valve with the black refrigerant cork tape, properly affix the sensing bulb to the evaporator core, and wrapped it with the black refrigerant cork tape. I only work on old car systems using R-12, and that stuff is so expensive that you don't want to make mistakes.

Update: I just read one of your replies, and realized that you only guessed at the proper amount of refrigerant oil. If I were doing that repair, I would have pulled the compressor and drained the oil, flushed the system with a refrigerant flushing agent, and blown it out with compressed nitrogen to make sure that the system was clean of any debris. Working on refrigeration is like a surgeon doing surgery, you have to have a clean environment and clean piping. If the system was open to the atmosphere, you have no idea of what might have gotten into it.
I only pulled vacuum for about 2h, and then waited for just about 1h before beginning the nitrogen cycles. So I did not vacuum-pump or wait anywhere near as long as you. If I end up evacuating and redoing the job, I will follow your routine instead.

I did properly affix the sensing bulb (put it in the same exact way it was inserted in the old evap), but I did not use refrigerant cork tape (on account of me not knowing it was a special type of tape). So it sounds like I should order some of this and fix that mistake.

I did indeed guess the proper amount of refrigerant oil. From what I knew at the time (or thought I knew after watching some youtube videos) this seemed like it would be ok. But maybe not.

The system was open to the atmosphere and it probably had been sitting like that for months.

Thanks for your advise.
 

btcfarmer

New member

Equipment
Kubota M7040, Kubota SVL 95-2S, Volvo EC290B
Apr 9, 2024
25
9
3
Central Florida
IF you used a rented vacuum pump then always replace the oil in the pump for best results removing moisture from the system. Always shut off all valves (manifold gauges and valves at pump) BEFORE shutting down the pump.

If the system held vacuum (28inHg) or better then you were fine. If you purged the lines correctly...then there should not have been any significant amount of air introduced.

Sounds like you charged it correctly. If the compressor were weak or failing it would show as low pressure on both the low and high side.

IF you had a restriction, you would see higher than normal high side pressure and lower than normal low side pressure (even going into vacuum).

As previously mentioned I would turn my attention first to air flow issues. Make sure the fan belt (if belt driven) is tight and not slipping. Make sure all components (Radiator, Condenser, oil coolers) are clean and do not have the fins bent or dirty.

And most importantly.....check the fan shroud to see that air is not escaping around it and the radiator.
I purchased the vacuum pump, so it had fresh oil in it. And 10-4 on closing valves before turning pump off.

The system did hold vacuum at 29-30inHg. I am pretty sure I got those things done right. But thinking now I should have left the vacuum pump on a lot longer.

Sounds like my compressor is in good shape.

Will definitely do my best to clean the components tomorrow.

I know some of the fins on the condenser are bent in. Is it a good idea to attempt to straighten them out with a tooth pick or similar?
 

DustyRusty

Well-known member

Equipment
2020 BX23S, BX2822 Snowblower, Curtis Deluxe Cab,
Nov 8, 2015
6,237
4,816
113
North East CT
You roll the dice and sometimes you get lucky. I remember my first venture into mobile air conditioning and all the mistakes that I made. I learned from my mistakes and was lucky enough to get properly trained in a United Delco training school for dealership technicians. The one thing that the instructor drilled into us was that you always have time to do the job over again, but it is better to take your time and do it correctly the first time every time. This is why I will evacuate for 24 hours because I am in no rush. I have updated my tools through the years, and I have learned some new "tricks" such as using a micron meter to determine how low you can draw down a system. Below are 2 readings that I got last summer working on a 1969 Cadillac. It was a challenging job since it held 5 pounds of R-12 refrigerant, and I didn't want anything to go wrong because I didn't have a recovery machine available at the time.
 

Attachments

  • Like
Reactions: 1 user

BAP

Well-known member
Lifetime Member

Equipment
2012 Kubota 2920, 60MMM, FEL, BH65 48" Bush Hog, 60"Backblade, B2782B Snowblower
Dec 31, 2012
2,756
869
113
New Hampshire
Definitely sounds like your heater control valve is leaking coolant by. Number 1 problem on ALL brands of tractors with AC systems blowing hot air after 30-60 minutes run time. The plastic shut off valve in the cab that controls flow of coolant through the heater leaks a tiny amount and causes the AC to get too hot and stop working properly. Easiest and cheapest fix is to put a shut off valve in the coolant line coming off the engine and keep it shut off unless you want heat. I have put in many of those over the years in many brands of equipment.
 

lugbolt

Well-known member

Equipment
ZG127S-54
Oct 15, 2015
5,207
1,893
113
Mid, South, USA
I'm still gonna lean towards compressor based solely on the pressure readings.

the high side, I'd like to see 220-250 on a warm day and then on the low side 25-30 after the cabin cools off. 30-35 with a warm cabin. Remember, pressure and temperature are closely related.

dumping water over the condenser is always going to drop the pressure-and with that, the temperature. Sometimes I thought about putting a washer pump and reservoir on my truck for this very reason.

i wonder if the clutch is failing? It could give similar symptoms of a slipping belt. I've run into this before on an L4240HSTC I think it was.

if the system was open a while, I would imagine that the system has debris in it which would further reiterate a possible compressor failure. Noone knows how long the system was open, and noone knows when/if the system was operated with a hole in it, which would allow the compressor to eat any dirt/dust and moisture. IIRC these don't have a HPCO, which would otherwise keep the compressor from running with zero psi in the system. AND who knows who's charged it, how they did it, and with what, in the past.

Since your low side is high and your high side is low, that would generally be indication of either a weak compressor or an expansion valve that is sticking or not working or maybe slippin belt or clutch, but again without being there it's hard to say for sure.
 
  • Like
Reactions: 1 user

number two

Active member

Equipment
B3030HSDC L2501HST
Mar 26, 2021
341
158
43
Northern Lower Michigan
Interesting thread!
OP has not posted back.
I'm thinking he found coolant leaking into the heater core was the problem.
He seemed well versed in AC repair!
 
  • Like
Reactions: 1 user

Tx Jim

Well-known member
Lifetime Member

Equipment
M7040 HDC-1,JD 4255,Ford 6700
Apr 30, 2013
1,199
128
63
Coyote Flats,Texas
All sorts of "possibles" mentioned, but before changing anything I would pinch off one of the heater hoses and try running like that for a while. See what difference that makes.
I recommend installing manual heater hose cut-off valve & adding some refrigerant while monitoring high side pressure gauge .
 
  • Like
Reactions: 1 user

btcfarmer

New member

Equipment
Kubota M7040, Kubota SVL 95-2S, Volvo EC290B
Apr 9, 2024
25
9
3
Central Florida
Cooling off the condenser with water shows that it needs more air flow through it.

You'll get it fixed with more cleaning.

Items like this help if you have the room between the radiator, oil cooler and condensor for them to fit. Can use water as well as air.
Thanks, I did purchase these and I definitely had a lot of gunk to clean out in all 3 coils (engine, oil, ac).

Unfortunately it did not resolve the problem, but this is a useful tool and I've cleaned all my other machines with it too, so thanks for the suggestion!
 

btcfarmer

New member

Equipment
Kubota M7040, Kubota SVL 95-2S, Volvo EC290B
Apr 9, 2024
25
9
3
Central Florida
Definitely sounds like your heater control valve is leaking coolant by. Number 1 problem on ALL brands of tractors with AC systems blowing hot air after 30-60 minutes run time. The plastic shut off valve in the cab that controls flow of coolant through the heater leaks a tiny amount and causes the AC to get too hot and stop working properly. Easiest and cheapest fix is to put a shut off valve in the coolant line coming off the engine and keep it shut off unless you want heat. I have put in many of those over the years in many brands of equipment.
I pinched the heating coolant hose off, and this made no difference unfortunately. Sounds like a great hack to put a shut off valve on the hose though. Is there an easy way to tell which is the input and which is the output of the two?

Apologies for the very late reply btw!
 

btcfarmer

New member

Equipment
Kubota M7040, Kubota SVL 95-2S, Volvo EC290B
Apr 9, 2024
25
9
3
Central Florida
I'm still gonna lean towards compressor based solely on the pressure readings.

the high side, I'd like to see 220-250 on a warm day and then on the low side 25-30 after the cabin cools off. 30-35 with a warm cabin. Remember, pressure and temperature are closely related.

dumping water over the condenser is always going to drop the pressure-and with that, the temperature. Sometimes I thought about putting a washer pump and reservoir on my truck for this very reason.

i wonder if the clutch is failing? It could give similar symptoms of a slipping belt. I've run into this before on an L4240HSTC I think it was.

if the system was open a while, I would imagine that the system has debris in it which would further reiterate a possible compressor failure. Noone knows how long the system was open, and noone knows when/if the system was operated with a hole in it, which would allow the compressor to eat any dirt/dust and moisture. IIRC these don't have a HPCO, which would otherwise keep the compressor from running with zero psi in the system. AND who knows who's charged it, how they did it, and with what, in the past.

Since your low side is high and your high side is low, that would generally be indication of either a weak compressor or an expansion valve that is sticking or not working or maybe slippin belt or clutch, but again without being there it's hard to say for sure.

First, apologies for the very slow response, and thanks for your reply.

I think you are right about the compressor being to blame. I have cleaned the whole system meticulously, and I have pinched the heating coolant hose, and I have verified no icing going on at or near the expansion valve.

I believe the compressor is indeed slipping. It turns over just fine when I first start the tractor up, but once it starts blowing warm air, I can see how it resists turning over, and stalls out for brief (0.1-0.2 seconds at a time), causing the wheel to get extremely hot from all the friction of the belt sliding across it instead of spinning it.

Meanwhile checking the gauges, I see that the pressure never gets much higher than ~210 psi.

I have a new compressor sitting in my workshop, and I am going to install it tomorrow.

Thanks for your help!
 
  • Like
Reactions: 1 user

btcfarmer

New member

Equipment
Kubota M7040, Kubota SVL 95-2S, Volvo EC290B
Apr 9, 2024
25
9
3
Central Florida
Interesting thread!
OP has not posted back.
I'm thinking he found coolant leaking into the heater core was the problem.
He seemed well versed in AC repair!
OP is sorry for not posting back sooner, ended up shelving the AC fixing project because a few much higher priority things came up. But I do apologize to everyone who responded with helpful advice so far in this thread, I should have dropped a note about it here.

But back on the project now, and about to put a new compressor in this machine. I hope that is the problem, because I have checked and crossed everything else raised here off already!
 
  • Like
Reactions: 1 user

btcfarmer

New member

Equipment
Kubota M7040, Kubota SVL 95-2S, Volvo EC290B
Apr 9, 2024
25
9
3
Central Florida
I recommend installing manual heater hose cut-off valve & adding some refrigerant while monitoring high side pressure gauge .
Yup, tried this, thanks. There was no difference. I have even ran the tractor with the seat+panel off and checked to make sure the heater core was not adding heat, butit doesn't.
 

Soopitup

Active member

Equipment
BX23S
Oct 25, 2018
341
159
43
New England
Just a few bullet points

-If you have a clog in your system it won't work at all. No flow.
The exception being if the condenser (or evaporator for that matter) is partially blocked.

-If you have a restriction you will have ice after the restriction. That's why the low side line coming off the evaporator is usually iced up, the expansion valve is a restriction (also a good indicator of how well the system is working).

-AC systems aren't as finicky as people think. A little bit of moisture in the system or the refrigerant being off a little bit won't prevent the system from working (cars have a pressure switch that doesn't allow the system to run if the pressure is too low, for example, and there's quite a bit of leeway there usually).
This is why autozone can get away with selling those recharge cans.
I'm not arguing for doing this, simply pointing out that your system seems to be beyond something as little as your charge being off a bit.
Same thing for bent fins on the condenser. A few won't make a difference, though it doesn't hurt to straighten them out. If you have a lot, or the fins are missing that's a different story.

-My first thought reading through this has been condenser airflow/cooling.
Are your fan blades dirty? A dusting won't matter, but buildup can effect how well the blades push air.
Is your ducting 100% complete and installed correctly? Over everything inline with the airflow? Air is lazy and likes to go around things like radiators/condensers.
Airflow should be able to hold a rag to the "front" side of the condenser/system.
How is the condenser temp? Does it gradually drop as you go down? There shouldn't be an sudden changes (that would most likely indicate a blockage).

I have zero experience with tractor AC specifically. A picture of the condenser area wouldn't hurt.
And if the factory ducting is lacking, it also wouldn't hurt to add some of your own.
 
  • Love
Reactions: 1 user

btcfarmer

New member

Equipment
Kubota M7040, Kubota SVL 95-2S, Volvo EC290B
Apr 9, 2024
25
9
3
Central Florida
Just a few bullet points

-If you have a clog in your system it won't work at all. No flow.
The exception being if the condenser (or evaporator for that matter) is partially blocked.
Thanks for your suggestions. I have gone over and done all this already though (fan blades were never too dirty but the condenser sure was).
I cleaned it, and I even installed two extra fans on a relay from the ac clutch wire to improve air flow. No luck.

But I have now determined beyond any doubt my problem was the compressor. I'm just about to update the thread on this. Hopefully someone else with my problem will find it useful.
 

btcfarmer

New member

Equipment
Kubota M7040, Kubota SVL 95-2S, Volvo EC290B
Apr 9, 2024
25
9
3
Central Florida
Update: I have taken the whole system apart.

Tl;dr: it was the compressors fault all along. It looked fine at first and second glance but it was not fine.

I opened the condenser and tested it with compressed air for blockage - there was none. I flushed it nevertheless and ran air through it for 40 minutes, to get rid of as much solvent as possible. Clean as a whistle now, but it was not the problem. Reinstalled and added oil.

Did the same for evaporator. I installed this myself a few months back and it was also clean. Reinstalled and added oil.

Cleaned all hoses. Reinstalled and added oil.

Took out compressor. Noted it had no oil at all in it. It is a wonder it didn't disintegrate. It was still turning and producing some pressure (and this is the reason I, inexperienced as I am, thought the compressor was OK before). It should be noted thr compressor did seize partially when machine got hot enough, but would appear to work fine when cold. I say partially seizing because it would still turn over, but miss a beat every second or so, and as a result, it got super hot from the friction as it opposed the belt.

So I installed a new compressor. Added it's oil. Then did the whole nine yards again with vacuuming for hours, letting it sit for hours to make sure no leaks, then I filled with about 150pai of nitrogen, let it sit again - no leaks. All systems check. Pulled vacuum and refilled with nitrogen a few more times just to really emphasize how serious I am about wanting a _cold_ ac with a perfect charge in this tractor.

So then I put the first can of refrigerant in. Let the vacuum pull it in. Then I start the tractor so I can put the rest of the refrigerant in and... the new compressor won't start LOL. Bad clutch I presume. Certainly nothing wrong wihlth wiring (my auxiliary condenser fans which are controlled from same circuit spinning happily).

So my latest lesson in AC school is: sometimes that cheap compressor that Amazon can deliver in 2 days is a POS.

Now waiting for another compressor, should be here tomorrow. Then I will do the whole vacuum-nitro-refill dance again.

And THEN I pray I will finally have cold air in this machine.
 
Last edited:
  • Love
Reactions: 1 user

DaveFromMi

Well-known member

Equipment
L3901 RCR1260
Apr 14, 2021
610
530
93
Indiana
You mentioned that there was no oil in the compressor. It is possible that the oil migrated to the condenser or evap. If you have excess oil in the system, it could affect performance as it it like an extra layer of insulation inside the tubes.
 

BAP

Well-known member
Lifetime Member

Equipment
2012 Kubota 2920, 60MMM, FEL, BH65 48" Bush Hog, 60"Backblade, B2782B Snowblower
Dec 31, 2012
2,756
869
113
New Hampshire
I hope that you have changed the expansion valve and put on a new drier. If not, change them before putting it back together.
 