Well the old faithful DeBillvis has given up the ghost for the last time. I mean really 22 years old it is time, so I am asking about these invertor generators,,, I get the 3 phase to AC then rectify it to DC to clean the wave form up and then invert it back to usable AC. The question is this, are the wave forms out of a regular gen set really that dirty? Anybody have one and what has been your findings,,, Yes tons of stuff on line, I however find it better to ask folks I know,,,,, more or less
 

85Hokie

Moderator
Staff member
Lifetime Member

Equipment
BX-25D ,PTB. Under Armor, '90&'92-B7100HST's, '06 BX1850 FEL
Jul 13, 2013
10,745
2,551
113
Bedford - VA
They can be that "dirty" for very sensitive stuff like computers - some motors will not like the softened square waves that are typically produced by low end invertors.
 

North Idaho Wolfman

Moderator
Staff member
Lifetime Member

Equipment
L3450DT-GST, Woods FEL, B7100 HSD, FEL, 60" SB, 743 Bobcat with V2203, and more
Jun 9, 2013
30,181
6,351
113
Sandpoint, ID
Most electronics like inverter power over a dirty generator power.
 
  • Like
Reactions: 1 users

GreensvilleJay

Well-known member

Equipment
BX23-S,57 A-C D-14,58 A-C D-14, 57 A-C D-14,tiller,cults,Millcreek 25G spreader,
Apr 2, 2019
11,400
4,899
113
Greensville,Ontario,Canada
'regular' generator... the output will be a real nice CLEAN sinewave.. tis the 'nature of the beast'.

'inverter' generator... output might be 'clean' or 'dirty' or in between. It'll vary from make to make, model to model, actual power being used. You need a spectrum analyzer ( you HAVE one right ?) to see what's happening......
 

DaveFromMi

Well-known member

Equipment
L3901 RCR1260
Apr 14, 2021
610
530
93
Indiana
The main advantage of inverter generators is fuel savings.
I recently got a Honda 3000iS. We lost power for a day and I ran 2 upright freezers, 1 small chest freezer, a large refrigerator and powered some electronics on it. It was quiet, but responded quickly to load changes. Used about 1.5 gallons of gas in 12 hours.
 
  • Like
Reactions: 1 users

The Evil Twin

Well-known member

Equipment
L2501, LA526,
Jul 19, 2022
2,814
2,825
113
Virginia
The only advantage over a good standard generator is fuel consumption and noise. I don't know about y'all, but none of my electronics run on AC power. Pretty much anything with a circuit board has an inverter in it. Laptop input is 110-240vac. Same for the TV and all the entertainment stuff. Fancy fridge? Same voltage requirements (it is a VSD compressor). The inverter folks scared everyone into thinking they will cause their iPad to burst into a nuclear flame without an inverter generator.
Fact is, a good "contractor" generator supplies power of the same quality that the utility does. I've run my entire house off of one for days. Solid 60hz and 119 vac from start to finish. Did your TV die when the power went out? If not then it survived dirty power. As did the fridge. Inverter generator are a feel good thing. I've never lost a single gadget in decades of RV living on a contractor grade open frame Generac gene.
 
Last edited:
  • Love
Reactions: 1 user

i7win7

Well-known member

Equipment
BX2370, B2650 grapple, tree puller, trailer mover, 3 point hoist, mower, tiller
Feb 21, 2020
3,379
3,982
113
Central, IL
The biggest problem with inverter gens is availability of replacement inverter when it dies. Sad to scrap a good engine when the electronics die.

I chose to buy an Ecoflow solar gen. It can go between the AC outlet and the device(s) you want to run during power failure, like a UPS box. I am impressed with these units and will replace all of my UPS units with Ecoflow Delta 2's.

I have the Ecoflow pro with extra battery running the pellet stove. This will be switched to air conditioner in a few months. The larger Ecoflow units can be paired with a smart gas gen. Gas gen has a 48v DC cable (and AC outlet) to charge solar gen batteries and can be controlled by the solar gen or phone app.

Solar panels can be added later if your happy with original setup (saves on gas/propane). Only time will tell if Ecoflow was a good investment.
 

GeoHorn

Well-known member
Lifetime Member

Equipment
M4700DT, LA1002FEL, Ferguson5-8B Compactor-Roller, 10KDumpTrailer, RTV-X900
May 18, 2018
6,039
3,316
113
Texas
Evil has said it….. There is no computer…not even one of the older desktops…which run without first internally modifying the AC with a power-supply that filters and cleans up the power.

I have a cheap, chineese copy ordinary contractor-type, open frame 3,000-watt generator I bought from Pep Boys when they decided they were no longer going to be a parts-store…. I paid $159 for new in the box…. It has run everything including all the accy’s in the Airstream trailer….which is the latest flat-screen digital TV, stereo, BlueRay, and the A/S LED lighting, 12V water pumps, Samsung convection/MicroWave… all supposedly “sensitive” electronics…. the AirConditioner, Furnace, refrigerator (digital circuit board controls)….been doing it for over 6 years without any problems whatsoever.

What do you think the power company uses? Water out of the dam-penstock spins a mechanical generator exactly like the typical portable generator.… “clean sine-wave” my arse !

Inverter/gennys are quieter, expecially when not having to put out max demand… but they are also more sensitive to issues that can introduce failure modes than contractor types…..after all…they introduce yet-another electronic device between the armature and the output receptacle. You could do the same thing by plugging your own converter-to-inverter into the system. What makes for more complication? IMO

If the noise isn’t an issue for you…I’d vote for the conventional portable.
 
  • Like
Reactions: 1 user

zuiko

New member

Equipment
L2900
May 29, 2017
13
3
3
Canada
You are correct that almost all electronic equipment today will accept a wide range of voltages and frequencies and will easily run on a conventional generator. The one exception is a UPS battery backup. It expects tight tolerances for the input and will disconnect if the frequency or voltage is beyond a set limit.

Frequency for a UPS typically needs to be within 5% of 60Hz, anything beyond that and it will disconnect from the power line. A regular generator produces a frequency that is dependent on the engine speed and easily has more than 5% variance, especially as the load changes. This is where an inverter generator will produce a cleaner signal that a UPS will accept.
 

The Evil Twin

Well-known member

Equipment
L2501, LA526,
Jul 19, 2022
2,814
2,825
113
Virginia
When sized correctly, the generator doesn't bog down enough for it to care. Hence, the reason data centers can run their UPS, servers, chillers, pumps, fans and vending machines on a generator. They don't use inverter generators. They are sized correctly.
The problem is when normal folk try to run their 6700 square foot house off of a 9kw Lowes special generator.
 

BruceP

Well-known member

Equipment
G5200H
Aug 7, 2016
851
368
63
Richmond, Vermont, USA
The one exception is a UPS battery backup.
Are you aware that a UPS is simply an inverter? (It converts the DC from battery into 60Hz sine-wave)

HENCE: It is kinda silly to have an 'inverter' generator feeding a UPS... the energy from the gasoline passes through 'processing' multiple times thus reducing efficiency at each step.

HOWEVER: Using a NON-inverter generator to feed a UPS for the most sensitive electronics is a good idea.

In this way, one can use NON-inverter generator to power refrigerator, freezer, furnace...etc.....then also feed thru UPS if there is a need for 'clean' power.


I do agree with others that the big advantage for inverter generator is fuel-savings.
The big DISadvantage for inverter generator is when it breaks.... repairs cost more than new machine.
 

Flintknapper

Well-known member
Premium Member

Equipment
L2350DT
May 3, 2022
1,764
2,216
113
Deep East Texas
The main advantage of inverter generators is fuel savings.
I recently got a Honda 3000iS. We lost power for a day and I ran 2 upright freezers, 1 small chest freezer, a large refrigerator and powered some electronics on it. It was quiet, but responded quickly to load changes. Used about 1.5 gallons of gas in 12 hours.
My Yamaha is the same way. Quiet, fuel miser, will run all the refrigerators and freezers, computer, TV's until the power came back on or I decided to get the 12Kw out. None of that matters now though since we went Generac 24K standby.

But yes, Inverter technology is nice to have.

Yamaha Gen3.jpg

I do agree with others that the big advantage for inverter generator is fuel-savings.
The big DISadvantage for inverter generator is when it breaks.... repairs cost more than new machine.
^^^^^

Buy a 'good' one.

Mine is 10 years old this past June and has at least 400 hours on it. Still running great. Always starts on the first pull. Very miserly on fuel. Not saying it is the right gen-set for everyone....but its been mighty good to me.
 
Last edited:
  • Like
Reactions: 1 users

zuiko

New member

Equipment
L2900
May 29, 2017
13
3
3
Canada
Of course large commercial gas/diesel generators will regulate the power sufficiently, but that's not what we're talking about here, I thought we were discussing the small portable generators.

As for why you would use a UPS with a generator, how else would you keep critical equipment running between the time the power goes out and the generator kicks in?
 

RCW

Well-known member
Lifetime Member

Equipment
BX2360, FEL, MMM, BX2750D snowblower. 1953 Minneapolis Moline ZAU
Apr 28, 2013
9,134
5,192
113
Chenango County, NY
This thread has been enlightening. I have a older 5.5k generator that is showing its age and limitation for capacity.

I had another thread about a portable generator ~ 10,000 watts.

Got thinking inverter was only way to go. Tough sledding at 9,000 watts or so. Expensive. $2-3,000, versus a contractor-type at ~$1-2,000.

After this thread - - thinking I should go back to a regular portable generator, and take inverter off the table.
 
  • Like
Reactions: 1 users

fried1765

Well-known member

Equipment
Kubota L48 TLB, Ford 1920 FEL, Ford 8N, SCAG Liberty Z, Gravely Pro.
Nov 14, 2019
7,843
5,066
113
Eastham, Ma
My Yamaha is the same way. Quite, fuel miser, will run all the refrigerators and freezers, computer, TV's until the power came back on or I decided to get the 12Kw out. None of that matters now though since we went Generac 24K standby.

But yes, Inverter technology is nice to have.

View attachment 97489


^^^^^

Buy a 'good' one.

Mine is 10 years old this past June and has at least 400 hours on it. Still running great. Always starts on the first pull. Very miserly on fuel. Not saying it is the right gen-set for everyone....but its been mighty good to me.
I have that EXACT same generator for backup here in Florida.
Have only used it twice in ten years, but it is a sweet little machine, and I will never surrender it.

I also have a Honda EM 6500 water cooled unit up North.
A truly wonderful piece of machinery!
 
  • Like
Reactions: 1 user

AndyM

Active member
Lifetime Member

Equipment
BX25DTLB
Sep 21, 2016
462
131
43
Vancouver Island Canada
You are correct that almost all electronic equipment today will accept a wide range of voltages and frequencies and will easily run on a conventional generator. The one exception is a UPS battery backup. It expects tight tolerances for the input and will disconnect if the frequency or voltage is beyond a set limit.

Frequency for a UPS typically needs to be within 5% of 60Hz, anything beyond that and it will disconnect from the power line. A regular generator produces a frequency that is dependent on the engine speed and easily has more than 5% variance, especially as the load changes. This is where an inverter generator will produce a cleaner signal that a UPS will accept.
I can attest to this - I have a UPS to protect my NAS, Routers et al - the old 9000 generac worked ok when new but the UPS kicked it out at one point. A new cheapo 11,500 unit seems to work with it fine (for now). Both are non inverter.
 

The Evil Twin

Well-known member

Equipment
L2501, LA526,
Jul 19, 2022
2,814
2,825
113
Virginia
Of course large commercial gas/diesel generators will regulate the power sufficiently, but that's not what we're talking about here, I thought we were discussing the small portable generators.

As for why you would use a UPS with a generator, how else would you keep critical equipment running between the time the power goes out and the generator kicks in?
If one has such critical equipment then they would already have a UPS. Generator type would not matter for it in any event. Sized appropriately, a standard unit would be fine. Any size- homeowner to business owner
Commercial/ industrial units don't regulate power. They regulate RPM and inherently, generate pure sine wave power. Power quality for "sensitive" equipment is done outside the generator with equipment that conditions the power from the utility also.
 

skeets

Well-known member

Equipment
BX 2360 /B2601
Oct 2, 2009
14,551
3,299
113
SW Pa
Thanks guys, looks like I am going to look for a plain everyday 10kva portable genset
 